Posted: 08/10/09 06:49pm Link  |  Print  |  Notify Moderator

I have a Onan BGE-4kw (spec J) generator in my Four Winds Class C. The generator starts and runs great, even under moderate load. The problem is when I turn on the A/C, the generator goes wide open and stalls. If I have someone manually keep the throttle from moving to wide open, it takes the load, never misses a beat and runs great.

The generator has had a recent tune up with a new oil/filter, fuel filter, air filter, fuel pump and spark plugs. The carb has been removed and was EXCEPTIONALLY clean, but a can of carb cleaner has also been run through the engine as well as a can of Seafoam. We've also adjusted the governor linkage (plastic ball/socket end of the throttle linkage) as per the service manual, but still no luck.

Any thoughts? I'm thinking maybe points or governor spring?

Thanks,
Dan

gunny357

North Carolina

Senior Member

Joined: 04/06/2005

View Profile


Offline
Posted: 08/10/09 07:14pm Link  |  Print  |  Notify Moderator

Sounds like it is running lean and can't take a full load.

A fresh set of point (if not electroninc ignition) would be the first thing I'd do.

dan_hardison

Delaware, OH

New Member

Joined: 08/10/2009

View Profile


Offline
Posted: 08/10/09 07:23pm Link  |  Print  |  Notify Moderator

gunny357 wrote:

Sounds like it is running lean and can't take a full load.

A fresh set of point (if not electroninc ignition) would be the first thing I'd do.
Thanks for the reply. Lean was my first thought as well, but I can manually rev the generator to wide open throttle and it takes the fuel with no problem (both with and without load).

I have a set of points on order (wish it was electronic).

Thanks,
Dan

Generator Jim

Conway, SC

Senior Member

Joined: 07/16/2005

View Profile



Good Sam RV Club Member

Offline
Posted: 08/11/09 02:24pm Link  |  Print  |  Notify Moderator

Dan
I don't think you have points.

ONAN started using electronic ignition with the spec G model. Your spec J should have an electronic module in between the engine and the generator at the top of the unit. Underneath the module is a plastic ring around the crankshaft with two arms that have magnets on them.
1. The module could have a bad ground. Place a double star washer under the back cap screw holding the module to the flywheel adapter.
2. The module could be bad. Test using procedure from service manual.
3. The trigger ring could be broken/shifted. Remove module and inspect using flashlight and rotate slowly using 3/8" Allen wrench in rotor bolt.
4. Coil could be going bad. Test using procedure in service manual.

JimL

* This post was edited 08/11/09 06:34pm by Generator Jim *


Jim & Jane Latour
08 Chevy 3500HD, crew cab, dually, Duramax/Allison
05 Wilderness Advantage AX6 365 BSQS, Onan 3.6KY
Retired AF CMS (E9) Power Generation and Onan RV genset Level III tech
Grand Strand Sams
Blog.rv.net

dan_hardison

Delaware, OH

New Member

Joined: 08/10/2009

View Profile


Offline
Posted: 08/11/09 06:22pm Link  |  Print  |  Notify Moderator

Generator Jim wrote:

Don
I don't think you have points.....
JimL

Thanks Jim, I was just about to click the 'place order' button for a set of point and condensor. So would a dying or out of adjustment electronic ignition module somehow force the carb to go wide open under load? Maybe something wrong out of adjustment with the governor or carb?

Thanks,
Dan

Generator Jim

Conway, SC

Senior Member

Joined: 07/16/2005

View Profile



Good Sam RV Club Member

Offline
Posted: 08/11/09 06:28pm Link  |  Print  |  Notify Moderator

A slight possibility of the trigger ring misalignment doing this.

I'd look at the float level before diving into the electronic stuff.

Secondary possibility is a split manifold. They are two piece with locating pins and silicone "glue". The glue sometimes gets brittle and falls out leaving a suction leak. Spray WD 40 on the joint. If engine speeds up, you've found your leak. Repair with High Temperature Silicone after a thorough cleaning.

The governor went to full throttle due to the engine slowing down. You are not getting the power you need at the generator.

JimL

* This post was edited 08/11/09 06:37pm by Generator Jim *

This Topic Is Closed  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Tech Issues

 > Onan generator issue - goes WOT then stalls under A/C load
Search:   Advanced Search

Search only in Tech Issues


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2014 Woodalls | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS