harper223

West Texas

Senior Member

Joined: 09/11/2008

View Profile


Offline
Posted: 11/13/09 08:03am Link  |  Print  |  Notify Moderator

I have a model narrowed down (Honda 3000) of generator for the travel trailer, and was going to use as a home backup as we typically lose power about 3x per yr/average.

This may sound like a silly question, because I have never owned a genny before. To run lights, refrigerator, computer, etc- do these individual appliances and the like plug directly into the generator? Is there some way to plug into 1 outlet (from the generator) to the house to power these things?

dalenoel

Howell, Michigan

Senior Member

Joined: 09/03/2007

View Profile



Good Sam RV Club

Offline
Posted: 11/13/09 08:15am Link  |  Print  |  Notify Moderator

There is and you will need a transfer switch to disconnect the power company grid from you and isolate your house. This is not something you want to do alone but would need a knowledgeable person.

In some localities you will need a permit as it is neccessary to protect the power company employees working on downed lines from you sending power to injure them.

Check with an electrician and you can get better local information.


04 Dodge RAM Quad Crew Cab 4x4
08 Jayco Eagle 322 FKS, Hensley Arrow, Prodigy Controller
Wife and I, Oreo the Malshi, and maybe a grandkid or two

downtheroad

Puget Sound

Senior Member

Joined: 02/18/2003

View Profile



Posted: 11/13/09 08:34am Link  |  Print  |  Notify Moderator

Take a look at this. It is full of info for your application and has supplies available also. Hope this helps

Home generator hook up info...LINK




"If we couldn't laugh we would all go insane"

GMC Duramax/Allison (LBZ)
Komfort 277TS .... Our Rig Picture
Reese Dual Cam HP
Lots of other stuff nobody cares about


harper223

West Texas

Senior Member

Joined: 09/11/2008

View Profile


Offline
Posted: 11/13/09 09:05am Link  |  Print  |  Notify Moderator

I'm assuming a manual transfer switch since the generator is portable. I would think that a fixed generator next to the house would use an automatic switch without you having to do anything in the event of a power outage. Our outages usually last about 4-24 hrs at the most, depending on the event. We had a tornado hit the next town 8 miles away and we lost power for about 4 days. Thats been the longest though.

wa8yxm

Wherever I happen to park

Senior Member

Joined: 07/04/2006

View Profile


Offline
Posted: 11/13/09 09:39am Link  |  Print  |  Notify Moderator

I put in a proper transfer switch.. But there are two ways to do it....

With the proper transfer switch you run ONE cable from the inlet on the back or side of the house to the generator (Or in my case the motor home) and then you flip switches and the house wiring distributs the power to the assorted loads (Computer, Television, Lights, including lights you can not unplug) this is the best way, simplest and easiest,, but of course the most costly.

Option 2 is a rat's nest of extension cords.. You bring a cord in via a door or window and run 'em across the floor's

This presents a tripping hazard, and of course the open door or window is a security risk for someone breaking in.

So... Take your pick

Some folks like to do things dangerous... I won't even tell you how they do it it's that dangerous.. I will say use one of the two methods above.


Nothin adds excitment like something that is none of your business
Kenwood TS-2000 housed in a 2005 Damon Intruder 377


camperpaul

Illinois Beach State Park

Full Member

Joined: 05/10/2006

View Profile


Offline
Posted: 11/13/09 11:43am Link  |  Print  |  Notify Moderator

The 3000 Watt generator isn't big enough to run the entire house. You probably have 100 Amp electric service.

Let's do the math:

240 Volts X 100 Amps = 24,000 Watts.

You might be able to get by with a 12,000 Watt generator if you watch your usage. That would be equal to the 50 Amp service in the RV parks.

The generator would have to be permanently installed and ideally run on natural gas, have automatic start and automatic change-over.

We're talking some big bucks here and the system is NOT a DIY project. You'll need an expert to install it for you.



Paul
Ham Radio - K9ERG (since 1956)
Campground host at IBSP (2006-2010)
Single - Full-timer
Coachmen Cadet 25
6.2L Diesel Suburban 1500


pinesman

virginia

Senior Member

Joined: 08/21/2006

View Profile


Offline
Posted: 11/13/09 12:46pm Link  |  Print  |  Notify Moderator

I have an outdoor disconnect which will power the house from the grid or generator, but not both at the same time. The way it is designed, the grid breakers can not be on at the same time as the generator breakers. It is complicated to explain but the generator can not backfeed to the grid. The downfall is that I have to manually cut off certain breakers in the main panel that my generator will not run. It might be cheaper than the regular transfer switch but still needs to be installed by a pro.

gstanton

Oakland, MD and Tierra Verde, FL

Senior Member

Joined: 01/25/2002

View Profile



Good Sam RV Club

Offline
Posted: 11/13/09 05:25pm Link  |  Print  |  Notify Moderator

I have used a 3500 watt genny for years to power our house in an outage. The math listed above of 24,000 watts is waaay off base. 3500 is not enough to run the whole house, but will run the furnace, microwave, television, refrigerator(s) and a bunch of lights. It's when the motors start-up that sucks the (watts). If we need to run the well pump, I switch off everything, pump up the water pressure, and switch the pump back off.

When I hit the lottery, I'll get a 7-8000 watt and we'll be good to go!


Dusty & Lindsay
Sadie the "Lassie" type Collie -13 yrs.
Maggie the Golden Retriever - 1 yr.
Oakland Maryland and Tierra Verde, FL
Our 3rd TT is an '02 26' Nomad Scout
Ford F150

Moderator

Bowling Green, KY

Moderator

Joined: 01/19/2004

View Profile



Posted: 11/13/09 06:26pm Link  |  Print  |  Notify Moderator

We are closing this one before suggestions that may get someone killed are posted..... as recommended earlier, get a qualified electrician for advice.

This Topic Is Closed  |  Print Topic  |  Post New Topic  | 

Open Roads Forum  >  Around the Campfire  >  General Topics

 > General generator question for home backup
Search:   Advanced Search

Search only in Around the Campfire


New posts No new posts
Closed, new posts Closed, no new posts
Moved, new posts Moved, no new posts

Adjust text size:

© 2010 Woodalls | Terms & Conditions | PRIVACY POLICY | YOUR PRIVACY RIGHTS